Reply To: Irrigation – Master Valves and Flow Sensors

#152348
Tyson Carroll
Participant

Yes you would think that but a main line break at 1 in the morning may not get noticed until 7. 6 hours of a mainline break running is a lot of water at 4 inches. Plus 4″ mains are notorious for popping of using PVC connection. Steel fittings are highly recommended as are saddles at your valves. 

Whether or not you have tried it the city’s preferred system will required meter’s fs/mv, power, and controllers is going to cost at least $40,000 more than a two-wire system and that is not including the labor for the wiring. 

In thinking about it further you might need multiple booster pumps regardless depending your available PSI since the pump will need to be tied into the controller or tie a central controller to the bp to turn on during your water window. 

What your describing could be done for $13,000-14,000 with 2-wire. 

Good luck!